Public Forums - Electronic Security
Main Moderator Mauricio Ramirez
Mauricio Ramirez
+506 7205 6170
San Jose
Costa Rica
Mauricio Ramírez specializes in electronic security systems, giving emphasis to correction of problems of configurations or installations, but without leaving aside the opportunity of new projects.

His company (Multiservicios Avanzados MyS) converges different systems and technologies, ranging from energy self-sufficiency to radio links, for which it has the certifications of various manufacturers.
Your welcome, Invited
Username: Password: Remember
  • Page:
  • 1

TOPIC: vedardalarm

vedardalarm #2585

From beginning to end, Vedard Security will guide you how to set up fire alarm system. Below is the steps to build a fire alarm system.

Part 1 Laying Pipeline

Common pipeline material: Electric tube pipe contains galvanized steel pipe, welded steel pipe, JDG steel pipe, KBG steel pipe and so on.

set up fire alarm system
fire alarm pipeline

Wiring types

the meaning of the various symbols labeld on common wire and cables

NH - Refractory, pass GB12666.6 refractory test;

ZR - Flame retardant, pass GB12666.5 bundle burning test

ZA / ZB / ZC - Flame retardant Class A / Class B / Class C

WD - Low smoke and halogen free

YJ - Cross - linked polyethylene insulation

V - PVC sheathed

S - Twisted pair

B - Single stranded hard line

R - Single stranded soft line

K - Control Cable

P - With shield

For example: WDZA-KYJY-7 * 1.5 - Low smoke halogen free flame retardant A grade XLPE double jacket 7 core 1.5mm2 cable control.

Common used wiring types:

At least flame retardant wire and cable should be used for weak-current line and fire-resistant cable should be used for the power supply line of the fire alarm system.

alarm circuit - ZR-RVS-2 * 1.5, NH-RVS-2 * 1.5, NH-RYJS-2 * 1.5 etc.

alarm circuit trunk - ZR-RVS-2 * 2.5, NH-RVS-2 * 2.5, NH-RYJS-2 * 2.5 24VDC

power line - ZR-BV-2 * 2.5, NH-BV-2 * 2.5, NH-BYJ-2 * 2.5 etc. 24VDC

power line trunk - ZR-BV-2 * 4.0, NH-BV-2 * 4.0, NH-BYJ-2 * 4.0

multi-line control circuit - ZR-KVV-N * 1.5, NH-KVV-N * 1.5 etc.

broadcast line - ZR-RV-2 * 1.5, ZR-BV-2 * 1.5, ZR-RVVP-4 * 1.5

telephone line - ZR-RVS-2 * 1.5, ZR-RVVP-2 * 1.5, NH-RVVP-2 * 1.5

open pump line - ZR-BV-2 * 1.5, ZR-RV-2 * 1.5, NH-BYJ-2 * 1.5 etc.

fire hydrant open pump feedback line - ZR-RV-4 * 1.5, NH-BYJ-4 * 1.5, ZR-KVV-2 * 1.5

network line - ZR-RVS-2 * 1.5, ZR-RVV-4 * 1.5, cat5 etc.

Sharing tube principle

principle: Different systems, different voltage levels, different current types of lines, should not be laid in the same tube or in the same slot.

For example: strong-current line and weak-current line should not share tube

broadcast line and other line should not share tube

telephone line and other line should not share tube

network communication line and other line should not share tube

alarm circuit line and 24V power line should not share tube

alarm circuit line and open pump line should not share tube

multi-line control line and alarm line circuit, 24V power line should not share tube.

Part 2 Equipment Installationfire alarm system circuit

1 Circuit types

There are circuit, T circuit, and mixed circuit

2-wire is used for the circuit, some equipment requires a circuit

Every circuit (loop) can have 100 point, 200 point, or 324 point etc. 10 ~ 20% margin should be left for each circuit

2 Detectors

detector types: point type (Photoelectric smoke, ion smoke, temperature, complex, UV flame, gas fuel, dual band, etc.)

line type (Infrared beam, recoverable / unrecoverable temperature sensing cable, air sampling, distributed fiber, light section, etc.)

conventional detector (non-coded) intelligent detector (coded) installation location: point type (distance between ceiling, roof, wall and height from the ground) line type (laying, distance between the roof, installation spacing) distance between other equipment and beam plate

3 Modules

surveillance module (input module, surveillance relay)

control module (output module, smoke exhaust relay)

combination module (input / output module, dual input module, dual output module, other combination module)

manual alarm button and fire hydrant button (coded / non-coded, telephone jack)

detector module (alarm relay, bus access module)

short circuit isolation module relay module (switch module)

fire repeater
fire repeater

Installation location: in module box

4 Fire display panel

types of fire display panels: 1) LED display 2) analog display panel 3) LCD display installation location of fire panel display on each floor of the fire panel display wiring: It is connected to fire alarm control panel via RS485 line.

5 junction box, module box

calculate the size of junction box and module box

determine the installation location of the junction box and module box

The modules should be set up centrally.



6 telephonetelephone fire alarmwiring fire alarm system

1) multi-line telephone system

N + 1 line system

2N line system

host capacity extension and jack

Bus telephone switchboard Multi - line telephone switchboard
fire telephone broadcastphone fire alarm

















7 broadcast

1) System components:

recording plate, regional control panel, power amplifier, module, speaker

Power amplifier power capacity selection: Capacity can not be less than 1.5 times the maximum capacity of broadcasts in the range of simultaneous broadcasts.

2) system mode: bus system, multi-line system

Bus-line broadcast system

Part 3 Equipment wiringwiring detectors

1 Wiring detector







2 manual alarm buttonfire modules

1) non-coded manual alarm button

2) coded manual alarm button

3) with jack and without jack

3 fire hydrant button

Fire hydrant button function requirements: Open pump, alarm, lighting

1) non-coded fire hydrant button

2) coded fire hydrant button

Wiring of the pressure switch is similar to that of the non-coded fire hydrant button, just without feedback lighting.


4 Surveillance module

equipment connect to surveillance module: 1) Water flow indicator 2) signal valve 3) non-coded fire hydrant button 4) fire damper 5) pressure switch 6) Water level monitoring 7) other feedback signals



6 Combination module

fire surveillance

Types of combination modules

1) single input / single output module (each with an address point or share an address point)

2) Dual input module (one or two address points)

3) Dual output module (one or two address points)

4) Dual input / dual output module

5) Three input modules

6) four input / two output modules

7) other combinations of modules

The location for the combination module:

1) Single input / single output module - air valve, fire doors, shutter doors, elevators and so on

2) Dual input module - flow indicator + signal valve, monitoring signal concentration

3) Dual output module - non-fire power cut, emergency lighting and so on

4) Dual input / dual output module - shutter doors and so on

5) Three input modules - monitor the signal concentration

6) Four input / two output modules - centralized monitoring and control (eg tower standard layer)

7) Other combinations of modules Smoke exhaust fire pump


7 multi-line control equipment

1) fire pump wiring

2) smoke exhaust fan wiring

Under normal circumstances, the rain valve group of electromagnetic valve, stage fire screen and other important fire facilities should also be set up multi-line linkage. Note: "Fire Regulations" only requires fire pumps and fire engines in addition to automatic control, the need for manual direct control.

Part 4 Fire control center equipment

1 Fire control center equipment introduction

1) fire alarm controller (wall-mounted, cubic up, piano-style)

2) fire alarm controller components (host panel, multi-line disk, bus, circuit cards, communication cards, etc.)

3) DC power supply plateaddressable fire alarm

4) fire broadcast and background music host

5) fire telephone host

6) CRT graphics display system

7) UPS uninterruptible power supply

8) Large space fire gun controller

9) electricity leakage fire alarm host

10) Level display

11) other equipment

2 the fire alarm controller capacity calculation Loop capacity (if the detector / module is coded differently)

Reserve capacity (consider fire partition)

Number of loops Combined with multi-line disc, the number of bus lines Controller capacity

3 multi-line disk, bus number number calculation 1) multi-line disc Number of linkage points (fire pumps, fire blowers, rain valves, etc.) the point number of each multi-line disk Linkage point arrangement Number of multi-line discs 2) bus number Number of linkage points (strong cut, emergency lighting, shutter doors, elevators, etc.) the point number of each bus-line disk Linkage point arrangement Number of bus-line discs

Note: fire regulation does not require the setting of a bus disk, but in order to facilitate the operation of some more important equipment (it has been set to multi-line linkage point without repeating the bus point), many projects will design the bus, combined with the control module. Commonly need to set the bus linkage point of the equipment are: non-fire power cut, emergency lighting, rolling doors forced landing, elevator landing, bell, fire valve reset.

Please Login o Create Account to join the conversation.

China Vedard alarm system www.vedardalarm.com
  • Page:
  • 1
moderators: latinpress, scamacho1, alex.e.garcia1, insetron, mrc.mauricio2, ceo17, alexpazos, sjaramillo1